Hydraulic testing of a dry system _________

Explanation:
During hydraulic testing of a dry system, the dry pipe valve clapper must be latch-open or removed so water can enter the dry piping and fill the system for the test. The clapper normally holds back water with air pressure, but for the test you need unobstructed water flow into the pipes to pressurize and inspect them for leaks. If the valve stayed closed, or was only throttled or locked in place, water wouldn’t fill the system properly, and the test wouldn’t accurately verify the system’s integrity.

During hydraulic testing of a dry system, the dry pipe valve clapper must be latch-open or removed so water can enter the dry piping and fill the system for the test. The clapper normally holds back water with air pressure, but for the test you need unobstructed water flow into the pipes to pressurize and inspect them for leaks. If the valve stayed closed, or was only throttled or locked in place, water wouldn’t fill the system properly, and the test wouldn’t accurately verify the system’s integrity.